Here's a crazy thought. Can I use a high power transformer like this instead of wiring a 220v circuit in my house?

https://www.110220volts.com/ar-10000.html?gclid=CjwKCAjwiaX8BRBZEiwAQQxGx-I14D3GBvcYlpWHJsEYBAyEJ3Yp9a1NFTqB9Iu16zCPo79Sd6qrXBoCi0QQAvD_BwE

The P134h uses 2800w and this unit is rated up to 10,000 which is much more than needed. Would something like this allow me to use a 110V 15A or 20A outlet to run the Effeuno?

Something tells me that this is wishful thinking and that I need at 30A outlet regardless of voltage but I'd love to know what you guys think.
« Last Edit: October 17, 2020, 01:43:53 AM by DoouBall »
Alex

Outdoor Oven: Blackstone. Indoor Oven: Gaggenau.

Online dragonspawn

  • Registered User
  • Posts: 69
  • I Love Pizza!
Re: Sanity Check - Effeuno, Roccbox, Zio Ciro Mini?
« Reply #101 on: October 17, 2020, 04:56:20 AM »
Here's a crazy thought. Can I use a high power transformer like this instead of wiring a 220v circuit in my house?

https://www.110220volts.com/ar-10000.html?gclid=CjwKCAjwiaX8BRBZEiwAQQxGx-I14D3GBvcYlpWHJsEYBAyEJ3Yp9a1NFTqB9Iu16zCPo79Sd6qrXBoCi0QQAvD_BwE

The P134h uses 2800w and this unit is rated up to 10,000 which is much more than needed. Would something like this allow me to use a 110V 15A or 20A outlet to run the Effeuno?

Something tells me that this is wishful thinking and that I need at 30A outlet regardless of voltage but I'd love to know what you guys think.

It is even worse. 30A may not be enough. Power = I*V, 2800/110 = 25.45 Amperes, that is what you need for the oven to work. 25.45 *100 / 30 = 84% . This mean you need converter with efficiency above 84% or you will overload your outlet. When increasing voltage this efficiency is hard to achieve.

Reading about US system - 240V outlets are pretty common it seems - for driers and the like. If they can deliver 3kw of power any reason not to use simple 15m extension cord that is rated for the load to the kitchen? It is not as if plugging and unpluging the drier is big deal.
« Last Edit: October 17, 2020, 05:11:41 AM by dragonspawn »

Offline apizza

  • Supporting Member
  • *
  • Posts: 805
  • Location: Wethersfield, CT
  • I Love Pizza!
Re: Sanity Check - Effeuno, Roccbox, Zio Ciro Mini?
« Reply #102 on: October 17, 2020, 08:09:54 AM »
While the transformer can increase the voltage it cannot increase the watts coming from the supply side. Even a 20 amp circuit is max at 2400 watts, not counting any losses.
Marty

Offline thezaman

  • Lifetime Member
  • *
  • Posts: 3544
  • Age: 67
  • Location: ohio
  • I Love Pizza!
    • lorenzos pizza
Re: Sanity Check - Effeuno, Roccbox, Zio Ciro Mini?
« Reply #103 on: October 17, 2020, 10:37:08 AM »
you need to have two separate 120 volt lines to make to work.

Online DoouBall

  • Registered User
  • Posts: 951
Re: Sanity Check - Effeuno, Roccbox, Zio Ciro Mini?
« Reply #104 on: October 17, 2020, 11:03:51 AM »
Ok that's what I thought - thanks!